Modbus value readout rs485

e:cue Forum Foren English Discussion Forums SYMPHOLIGHT (E) Modbus value readout rs485

Schlagwörter: 

Dieses Thema enthält 3 Antworten und 2 Teilnehmer. Es wurde zuletzt aktualisiert von Christoph Paduch Christoph Paduch vor 10 Monate, 3 Wochen.

  • Autor
    Beiträge
  • #246553

    Robbert Mak
    Teilnehmer

    Hi,

    Another question:
    I have to read a Modbus value (rs485) from a power meter (hager EC367M) and show usage in an actionpad.
    Can I do this with the sympl serial node?

    Robbert

  • #246555
    Christoph Paduch
    Christoph Paduch
    Moderator

    Hi Robbert

    With the SYMPL serial Node you can communicate over an RS232 and an RS485 interface.
    We do not provide libraries regarding the commands of different connectable devices, in your case the hager power meter.
    But you can send binary values to the connected device and also receive messages.
    Here it might be helpful to parse the messages in a C# script with the scripting engine.

    I hope, this helps.


    Freundliche Grüße / Kind regards
    Christoph

    • #246556

      Robbert Mak
      Teilnehmer

      Thanks, all we need to do is get a number (power usage) out of the meter and show it in the actionpad.
      I’ll guess it should be doable.

      Will give it a try.

  • #246577
    Christoph Paduch
    Christoph Paduch
    Moderator

    Ahh, one hint.
    In the actual firmware the parities “even” and “odd” are switched.
    So if you need a parity bit and it does not work, try the other setting.


    Freundliche Grüße / Kind regards
    Christoph